    Posted: February 08 2014 at 9:48am
What size generator would I need to keep a tank running during a power outage (or how do I calculate)? I have a 65g using about 500 watts. They seem to be rated for a running watts amount?

2 ecotech radions so about 300 watts
2 ecotech mp10s so about 36 watts
3 koralias nano 425 power heads so about 11 watts
12w skimmer pump
3 small pumps for reactors cobalt mj 900 so about 36 watts
50 watt heater
55 watt return pump
2 Brs dosing pumps negligible watts

Total 500 watts (if that even helps, sorry I'm a CPA not an electrician)

I'm not looking for a generator to live through the apocalypse or run anything else in my house, I'm just wanting a "oh crap power is going to be out for 6 hours to a few days" and I want to run just my tank (I can go elsewhere for living but my tank can't). Can anyone tell me a size range of a generator aka minimum not maximum that would work and save me a Saturday of google research? Thanks!

Edited by Bryce - February 08 2014 at 10:11am
65g Reef
Back to Top
badfinger View Drop Down
Guest
Guest


Joined: May 18 2009
Location: Murray, UT
Status: Offline
Points: 2079
Post Options Post Options   Thanks (0) Thanks(0)   Quote badfinger Quote  Post ReplyReply Direct Link To This Post Posted: February 08 2014 at 9:58am
i have a honda eu2000 generator... very quite and reliable. 1 gallon of gas runs it for about 8-9 hours
Back to Top
bmac2 View Drop Down
Guest
Guest
Avatar

Joined: August 18 2012
Location: Riverton
Status: Offline
Points: 683
Post Options Post Options   Thanks (0) Thanks(0)   Quote bmac2 Quote  Post ReplyReply Direct Link To This Post Posted: February 08 2014 at 10:01am
just running 2 tanks listed, and that equipment, if you are wanting to ONLY run your tanks, almost any generator made will do that.  You will need to have a power cord long enough to run to only the tank with the generator outside.
Aquarium Creations 300 gallon tank
Stand by Dion
Back to Top
Bryce View Drop Down
Guest
Guest
Avatar

Joined: May 25 2012
Location: Lehi
Status: Offline
Points: 1113
Post Options Post Options   Thanks (0) Thanks(0)   Quote Bryce Quote  Post ReplyReply Direct Link To This Post Posted: February 08 2014 at 10:11am
Thanks guys just wanted to be sure I wasn't missing something with the rated vs running and yes my tank in in basement by a walkout door to backyard.
65g Reef
Back to Top
Akira View Drop Down
Paid Member
Paid Member
Avatar

Joined: September 11 2011
Location: Tooele
Status: Offline
Points: 1640
Post Options Post Options   Thanks (0) Thanks(0)   Quote Akira Quote  Post ReplyReply Direct Link To This Post Posted: February 09 2014 at 3:59am
Just to make the math simple every 100 watts = about 1 amp.  The rating on a circuit is 80% of the breaker rating , so on a 20 amp breaker 16 amps is about the max you want to have on the circuit  to prevent it from tripping when there is a peak in the load . Peak in the load could be a microwave, hair dryer etc turning on as it increases the amp load for a few seconds on start up. So you have 500w you want to run, a 600w would be the smallest you should run without any issues  .  you could almost run an inverter off of your car for that small of an amount. Hope that kind helps with the rating system. 
Back to Top
DLindquist View Drop Down
Guest
Guest
Avatar

Joined: June 07 2008
Location: Lehi
Status: Offline
Points: 1573
Post Options Post Options   Thanks (0) Thanks(0)   Quote DLindquist Quote  Post ReplyReply Direct Link To This Post Posted: February 09 2014 at 7:46am
I would also add that during a power outage, running your entire set up should not be necessary. You simply want to save your livestock. Utilizing heaters and pump should be your main concern. 
A government strong enough to give you everything you want, is powerful enough to take everything you have.

Back to Top
laynframe View Drop Down
Guest
Guest
Avatar

Joined: May 17 2009
Location: north ogden
Status: Offline
Points: 1062
Post Options Post Options   Thanks (0) Thanks(0)   Quote laynframe Quote  Post ReplyReply Direct Link To This Post Posted: February 09 2014 at 11:06am
50 watt heater seems pretty weak. If your home goes with out power during the winter I think the heater wouldn't maintain. Also consider running dual heaters in case one fails. Just my 2 cents.
The time we enjoy wasting isn't wasted time!!!!
Back to Top
bmac2 View Drop Down
Guest
Guest
Avatar

Joined: August 18 2012
Location: Riverton
Status: Offline
Points: 683
Post Options Post Options   Thanks (0) Thanks(0)   Quote bmac2 Quote  Post ReplyReply Direct Link To This Post Posted: February 09 2014 at 11:23am
I guess my question is why are you looking at generator specifically?  The batter backup systems we use for computers can run your circulation pumps and heater for many hours.  If you want your return pump going, do two of them, one for the pump, one for the heater and circulation pumps.  That is all you need.  No lights, etc.  It is about saving the livestock.  It does NOT hurt them at all to go a day or so without the lights going.  AND, they sit hooked to your house power, stay charged and automatically take over when the power goes out.  NO cranking generator, no fuss, no muss.   I have 2 big generators, I could probably run my entire house with them, but I have batter backup on my mp60 so it stays running in case of power failure.